Grounding the shore power line?

The shore power setup on my boat is pretty primitive-looking: there is only a two-conductor Romex-looking wire running from a standard shore power plug in the cockpit directly to a GFC-protected outlet in the cabin. There is no AC panel, nor breaker, nor even switch in the circuit.

At the very least, shouldn't there be a ground wire in there? And if so -- and I hadn't ever thought of this before -- is it kosher to ground 110v AC to the same ground as your 12v DC? I can't figure how you could do otherwise in a boat, but it seems wrong, somehow.
Reply With Quote
  #2   IP: 64.25.5.225
Old 08-26-2008, 01:37 PM
policecentral policecentral is offline
Senior Member
 
Join Date: Jun 2007
Location: Atlanta, GA
Posts: 56
Thanks: 0
Thanked 0 Times in 0 Posts
Ground Wire

If I understand, you have only a single outlet for 110v. However, it certainly should connected to shore power connector by a three wire, grounded wire. Copper (or green) wire is ground, white wire is neutral, black wire is hot. Connect to same wires at the SP connector.

Also, you should buy a small fuse box, and put in a 15 amp fuse for 14ga wire, or a 20 amp fuse for 12 ga wire to the outlet. As you are presently connected, you have no fuse excepting the shore power supply that is probably 50-100 amp or so. This is a dangerous situation.

Also, check your shore power cable to make sure it is three wire, grounded as well. When you have completed this, you can buy an inexpensive ground tester, three light gadget to plug into your outlet to check it out. Your gfi as presently connected with no ground is useless.

You can ground to a convenient bolt on your engine -- I use a bolt on the flywheel cover. All grounds are the same, 12v, 110v.
Reply With Quote
  #3   IP: 207.34.223.165
Old 08-26-2008, 01:59 PM
Bob.Griffin Bob.Griffin is offline
Senior Member
 
Join Date: Jun 2007
Posts: 47
Thanks: 0
Thanked 4 Times in 4 Posts
I'm not the greatest expert on shore power installations but I'd be a bit wary of connecting the 110 v shorepower ground to your 12 v ground, who knows what stray currents may occur and cause galvanic problems. As I understand it, you only need a good ground for the 110 v shore supply when you are actually plugged into shore power, and this ground MUST be the third ground wire that should run from the boat 110 outlet(s) all the way to the shore outlet you plug your shore power cable into. When you are not connected to shore power, you don't need any grounding on the boat, because the 110v circuit is dead. I agree with 'policecentral', you definitely need a fuse and a switch, preferably marine quality.

Bob (s/v Saga)
Reply With Quote
  #4   IP: 142.68.124.246
Old 08-26-2008, 04:14 PM
rigspelt's Avatar
rigspelt rigspelt is offline
Afourian MVP
 
Join Date: May 2008
Posts: 1,186
Thanks: 0
Thanked 19 Times in 17 Posts
Some sources I found useful for AC wiring on boats:
http://www.boatus.com/boattech/casey/36.htm
http://seagrant.uaf.edu/bookstore/bo...cal-safety.pdf
Also Nigel Calder's Boatowner's Mechanical and Electrical Manual and Wing's Boatowner's Illustrated Electrical Handbook.

Last edited by rigspelt; 08-27-2008 at 06:03 AM.
Reply With Quote
  #5   IP: 65.213.83.111
Old 08-27-2008, 05:44 AM
jhwelch's Avatar
jhwelch jhwelch is offline
Senior Member
 
Join Date: Dec 2005
Posts: 476
Thanks: 0
Thanked 6 Times in 6 Posts
My boat is not wired for AC, so for the times that I am at a dock I
just run an extension cord so I can use the computer or charge
a cell phone, etc.

If you only have that one outlet a cord might be less trouble than
adding a circuit breaker, etc. for the few times(?) you need electricity.

-jonathan
Reply With Quote
  #6   IP: 206.181.246.34
Old 08-27-2008, 09:03 AM
SEMIJim SEMIJim is offline
Senior Member
 
Join Date: Oct 2007
Posts: 129
Thanks: 0
Thanked 1 Time in 1 Post
Quote:
Originally Posted by Bob.Griffin View Post
I'm not the greatest expert on shore power installations but I'd be a bit wary of connecting the 110 v shorepower ground to your 12 v ground,
Where else would you connect it? It's ground. That's where it has to go.


Quote:
Originally Posted by Bob.Griffin View Post
who knows what stray currents may occur and cause galvanic problems.
There had better be none in the ground wire. If there is: Something is badly broken and the shore power connection is dangerous and should not be used under any circumstances.

Not only should you have a fuse or breaker on the boat, as close as possible to the shore power inlet, but all 120VAC fixtures should be GFCI-protected. (Something I have Yet To Do on our boat.)

Jim
Reply With Quote
  #7   IP: 63.239.69.1
Old 08-27-2008, 09:46 AM
Baltimore Sailor's Avatar
Baltimore Sailor Baltimore Sailor is offline
Afourian MVP
 
Join Date: May 2007
Location: Monrovia, MD
Posts: 640
Thanks: 0
Thanked 6 Times in 6 Posts
Quote:
Originally Posted by jhwelch View Post
My boat is not wired for AC, so for the times that I am at a dock I
just run an extension cord so I can use the computer or charge
a cell phone, etc.

If you only have that one outlet a cord might be less trouble than
adding a circuit breaker, etc. for the few times(?) you need electricity.

-jonathan
True. But the system is there on my boat, and my OCD won't let me not make it work as it should. I am helpless.
Reply With Quote
  #8   IP: 207.34.223.165
Old 08-27-2008, 10:30 AM
Bob.Griffin Bob.Griffin is offline
Senior Member
 
Join Date: Jun 2007
Posts: 47
Thanks: 0
Thanked 4 Times in 4 Posts
Bob: I'm not the greatest expert on shore power installations but I'd be a bit wary of connecting the 110 v shorepower ground to your 12 v ground,

SEMIJim: Where else would you connect it? It's ground. That's where it has to go.

Bob: The AC ground has to be onshore where you plug in your shore power cable. Electrical generation companies go to great expense to ensure every 110 v AC service is properly grounded within their infrastructure. The ground wire is provided in the event that an electrical appliance short circuits, and instead of electrocuting the user, the short circuit should go to ground. This is another reason I would avoid grounding to an engine block, this may not be an effective ground to avoid electrocution in the event of a faulty 110v electrical device on board. BTW, I totally agree that all onboard outlets must be GFCI types that trip the power in the event of water/moisture incursion.

Bob (s/v Saga)
Reply With Quote
  #9   IP: 192.60.230.155
Old 08-27-2008, 12:03 PM
High Hopes's Avatar
High Hopes High Hopes is offline
Afourian MVP
 
Join Date: Feb 2008
Location: Fairfax, VA
Posts: 530
Thanks: 0
Thanked 1 Time in 1 Post
Hello Police Central,

GFI’s work with or without a ground connection. They work by comparing the difference between the current in the hot wire and the current in the neutral wire. These currents should be exactly the same. If they are not, then some stray current is going somewhere – like through your heart. Typically a stray current is from the hot lead to earth (ground). The neutral wire is already at or near earth potential, so it is harder to develop a stray current between the neutral wire and a ground.

Schematics of actual GFI circuits show no involvement of the green ground wire. Not only that, a GFI can be reverse wired with respect to hot and neutral, and it will still function properly.

Hi Balt,

I do not connect the ground wire to anything except the AC receptacles (which should be three pronged). This proves protection form a faulty piece of AC equipment. However, ABYC recommends connecting the AC ground to the engine (and hence the 12 volt system).

These two different schools of thought are both based on failure mode analysis. The ABYC approach recognizes that any equipment connecting the AC to the 12 volt system – such as a charger – can cause a problem. The charger could short and cause the 12 volt ground to be hot with 110 Volts. If this happens, either the circuit breaker or the GFI will trip.

The other school of thought (not really mine) argues that if you ground the AC system to the 12 volt system, then any device that uses the 12 volt power now provides a ground point for electrocution should an AC appliance fault. There are more things to short to lurking about on the boat. If the 12 volt system is truly isolated, there can be no shock.

This method provides advantages in lightening protection systems and requires that the rigging also be isolated from the AC and 12 volt supplies. Stray marina currents, including mis-wiring of other boats, will not cause galvanic corrosion. Galvanic isolators are not even used. Through hulls are not bonded and therefore not subject to galvanic corrosion.

In defense of ABYC, it takes less work to check for a proper installation. The other scheme requires one to make sure that three systems are truly isolated (AC, 12 volt, rigging/sea water). If they are not, it can be a non-trivial task hunting down the problem. System isolation should be checked periodically as a maintenance item.

If you really want to do it right, you can buy an isolation transformer and have the best of all worlds. With one of these, you can hold the black wire, or white wire, and jump into the sea. Just don’t grab both of them at the same time. You won’t need galvanic isolators, galvanic erosion rates will be greatly reduced, and you will be in a position to install a modern lightning protection system. These transformers are now available with isolation test circuits built into them so they will tell you when something is amiss.

Bob,

Regarding electric company infrastructre, ground is typically a copper stake in the ground next to utility poles with transformers on them. It really is the earth. In marinas, it is earth under the water.

Steve

P.S. Balt, shouldn’t it be CDO with the letters in the right order the way they are supposed to be?

Last edited by High Hopes; 08-27-2008 at 12:17 PM. Reason: typo
Reply With Quote
  #10   IP: 64.25.5.225
Old 08-27-2008, 12:12 PM
policecentral policecentral is offline
Senior Member
 
Join Date: Jun 2007
Location: Atlanta, GA
Posts: 56
Thanks: 0
Thanked 0 Times in 0 Posts
Ground

Sorry to cause so much discussion, but "ground is ground is ground". Period. Power coming from the power plant is grounded, as is the supply line going to your house, as is properly installed shore power at the point it leaves land to the dock, and as it enters your boat and is grounded to the engine. These various points simply put a ground point close by the end use, your outlet. Stray currents will not come through your ground wire -- they will be "grounded out" via all the ground points above. And attaching all grounds to your engine insures that your shaft, zincs and propeller will all be "commonly grounded" and your engine will not be a "floating" (unconnected) ground -- thus you minimize electrolysis.

The is no such thing as a "separate" or "isolated" ground. It is all the same: "ground" (from whence it takes its name).

Regarding using an extension cord, we all have done that. But just be aware that it could be fused by shore power at pretty high amps -- if you have a short circuit that would potentially burn up the extension cord and could start a fire before it trips the fuse or breaker. Use Caution!


JSM
Reply With Quote
  #11   IP: 64.25.5.225
Old 08-27-2008, 12:15 PM
policecentral policecentral is offline
Senior Member
 
Join Date: Jun 2007
Location: Atlanta, GA
Posts: 56
Thanks: 0
Thanked 0 Times in 0 Posts
GFIs

To SteveM,

Thanks for info on GFI, as I don't know much about them.

I have never used them, and have not been convinced that I ever will. Lots of people seem to like them, but I never felt the urge to put them in anywhere.

JSM
Reply With Quote
  #12   IP: 206.181.246.34
Old 08-27-2008, 12:28 PM
SEMIJim SEMIJim is offline
Senior Member
 
Join Date: Oct 2007
Posts: 129
Thanks: 0
Thanked 1 Time in 1 Post
Quote:
Originally Posted by Bob.Griffin View Post
The AC ground has to be onshore where you plug in your shore power cable.
Yes. But just as with electrical appliances and tools that are not "double-insulated": The metal bits in your boat should be grounded so as to prevent them becoming energized.

Quote:
Originally Posted by Bob.Griffin View Post
Electrical generation companies go to great expense to ensure every 110 v AC service is properly grounded within their infrastructure.
No they don't. Electricity supply companies' responsibility for the wiring ends at the service entrance. (Usually where the meter is located.) Just as telephone service providers usually terminate their responsibility at a point called a "NID" (network interface device), aka: "demarc" (for demarcation point). Back to electrical service: What is supplied to your meter, and thence to the distribution panel (aka: fuse or breaker box) in U.S. residential situations is almost always single-phase, center-tapped 240VAC. There are three wires: L1, L2 and neutral. Neutral is nominally at ground potential, but it is not ground and is not to be treated as such. True ground is supplied by a separate ground rod, usually driven near either the meter or the distribution panel. Ground and neutral are commonly bonded inside the distribution panel. (But still: Neutral is not to be treated as ground, and vice-versa.)

Business/commercial systems are usually quite a bit more complicated. There's no way to describe them as simply as common residential service, because there are just too many options/variables. But still: The power company does not supply "ground."

N.B.: I am not a licensed electrician, nor do I play one on T.V.

Jim
Reply With Quote
  #13   IP: 207.34.223.165
Old 08-27-2008, 01:48 PM
Bob.Griffin Bob.Griffin is offline
Senior Member
 
Join Date: Jun 2007
Posts: 47
Thanks: 0
Thanked 4 Times in 4 Posts
I think Steve Markowski hit the nail on the head, for easier troubleshooting, better to keep all 3 electrical systems totally separated (12v dc, 110v ac and rigging etc grounding) and/or use an isolation transformer.

Bob (s/v Saga)
Reply With Quote
  #14   IP: 206.181.246.34
Old 08-27-2008, 01:55 PM
SEMIJim SEMIJim is offline
Senior Member
 
Join Date: Oct 2007
Posts: 129
Thanks: 0
Thanked 1 Time in 1 Post
Quote:
Originally Posted by SteveMarkowski View Post
Hello Police Central,

GFI’s work with or without a ground connection.
But the little test button won't

Jim
Reply With Quote
  #15   IP: 206.181.246.34
Old 08-27-2008, 02:08 PM
SEMIJim SEMIJim is offline
Senior Member
 
Join Date: Oct 2007
Posts: 129
Thanks: 0
Thanked 1 Time in 1 Post
Quote:
Originally Posted by policecentral View Post
Sorry to cause so much discussion, but "ground is ground is ground". Period. Power coming from the power plant is grounded, as is the supply line going to your house,
All incorrect. The power running in the lines up in the air, or buried in the ground (or under water, sometimes), is not "grounded." And, while it could be said to be "referenced to ground," what the power company leads to a customer premises is not "ground," per se. Even when there is a conductor that may be at the same potential as the ground, that line is actually called "neutral" and, as I stated earlier: Is not, nor can it be treated as, ground.

Quote:
Originally Posted by policecentral View Post
The is no such thing as a "separate" or "isolated" ground. It is all the same: "ground" (from whence it takes its name).
Wellll... that's not strictly true. But, for the purposes of this discussion: Yeah.

Reminder: I am not a licensed electrician, nor do I play one on T.V.

Jim
Reply With Quote
  #16   IP: 69.137.234.85
Old 08-27-2008, 05:31 PM
blackdove blackdove is offline
Senior Member
 
Join Date: Mar 2008
Posts: 32
Thanks: 0
Thanked 0 Times in 0 Posts
It's really a matter of code

All electrical and boating codes are clear...all grounds go together at one point, preferably from one buss bar of AC and one buss bar of DC to a common, single point. This does not include the white neutral wire, etc.

Hope this helps. If need be, I'll get out my code books and cite chapter and verse, but the easiest way to arrive at the same answer is to contact a licensed marine electrician. They will tell you the same thing. Thank you.

Blackdove
Reply With Quote
  #17   IP: 192.60.230.155
Old 08-27-2008, 05:55 PM
High Hopes's Avatar
High Hopes High Hopes is offline
Afourian MVP
 
Join Date: Feb 2008
Location: Fairfax, VA
Posts: 530
Thanks: 0
Thanked 1 Time in 1 Post
Wowie-zowie, what have we started.

SEMI Jim,

The little test button on a GFI will work without a ground connection. It will also work with the power leads (black and white) swapped. I tested this operation. The circuit design supports this. The little green light works, too. The ground isn’t used anywhere except for the third connection for the socket and to bond the mounting hardware.

Police Central,

Every telephone pole transformer provides isolation. High tension transmission does not involve any specific ground circuit; it involves electrically isolated transmission circuits established between transformers. The transformer windings are grounded to the earth by connecting the center taps to a rod in the earth. This was originally done to prevent static charge build up on the transmission wires which would otherwise probably kill more people than the actual transmission tension.

Bonding everything on the boat promotes corrosion in hot marinas. Electric currents always take the path of least resistance. So if there is a current under your boat from stem to stern, currents will enter the first underwater metallic fitting, run through the bonding conductors, and exit out the rear-most underwater metallic fitting. This path is a better conductor than the water itself. I'm not sure this is actually galvanic corrison which can occur when two different metals come in contact. I suspect the mechanism it is more along the lines of electrolysis.

Years ago, when marinas weren’t hot, this wasn’t an issue. It isn’t as issue at sea where there are no electric currents in the water.

Black Dove,

Grounds should be wired to a single point. But I think the benefits to be had by connecting the AC ground with the 12 volt ground are marginal, especially if the 12 volt system is connected to the rigging.

Steve

Last edited by High Hopes; 08-27-2008 at 06:07 PM. Reason: additional info
Reply With Quote
  #18   IP: 69.137.234.85
Old 08-27-2008, 07:56 PM
blackdove blackdove is offline
Senior Member
 
Join Date: Mar 2008
Posts: 32
Thanks: 0
Thanked 0 Times in 0 Posts
Ground Central

Hi Steve,

The interconnection of the rigging is really bonding, not grounding and is intended for a different purpose although it could serve as a ground. The common ground, should include both ac and dc. I'm looking for the article I have that explains this a heck of a lot better than I ever could. My recollection is that Gordon West wrote it and it is really understandable and makes sense. When I find it I'll send it to folks who are interested in it privately rather than take up a lot of room in the eroom. Thank you.

Blackdove
Reply With Quote
  #19   IP: 76.106.5.221
Old 08-27-2008, 11:15 PM
Baltimore Sailor's Avatar
Baltimore Sailor Baltimore Sailor is offline
Afourian MVP
 
Join Date: May 2007
Location: Monrovia, MD
Posts: 640
Thanks: 0
Thanked 6 Times in 6 Posts
Quote:
Originally Posted by SteveMarkowski View Post
P.S. Balt, shouldn’t it be CDO with the letters in the right order the way they are supposed to be?
OCD = Obsessive Compulsive Disorder.

I have no idea what CDO might be. Chief Diving Officer?
Reply With Quote
  #20   IP: 70.108.145.220
Old 08-28-2008, 02:10 AM
High Hopes's Avatar
High Hopes High Hopes is offline
Afourian MVP
 
Join Date: Feb 2008
Location: Fairfax, VA
Posts: 530
Thanks: 0
Thanked 1 Time in 1 Post
it's a joke
Reply With Quote
  #21   IP: 206.181.246.34
Old 08-28-2008, 09:14 AM
SEMIJim SEMIJim is offline
Senior Member
 
Join Date: Oct 2007
Posts: 129
Thanks: 0
Thanked 1 Time in 1 Post
Quote:
Originally Posted by SteveMarkowski View Post
Wowie-zowie, what have we started.

SEMI Jim,

The little test button on a GFI will work without a ground connection. It will also work with the power leads (black and white) swapped. I tested this operation. The circuit design supports this. The little green light works, too. The ground isn’t used anywhere except for the third connection for the socket and to bond the mounting hardware.
Obviously I have assumed something, here. I assumed those test circuits were actually simulating a ground fault. I just did a quick bit of research. You're right: They're not. That's mildly disappointing.

So you could have a GFCI outlet with a ground connection that, in fact, has no (functional) ground, plug into it a non-double-insulated device, have an internal fault in that device that results in hot connected to a metallic case, and the only thing that will save your butt is the GFCI's electronics.

Jim
Reply With Quote
  #22   IP: 63.239.69.1
Old 08-28-2008, 10:26 AM
Baltimore Sailor's Avatar
Baltimore Sailor Baltimore Sailor is offline
Afourian MVP
 
Join Date: May 2007
Location: Monrovia, MD
Posts: 640
Thanks: 0
Thanked 6 Times in 6 Posts
Quote:
Originally Posted by SteveMarkowski View Post
it's a joke
Ah, I get it now. Slow brain day.

Have we reached a consensus yet? It seems to me that so far we've established that if one has no mixed-voltage equipment, e.g. inverters, on board, using the shore ground for the AC system is OK. However, if you do have an inverter on board the AC must be grounded internally.

Does that sound right? Some of the conversation has gone over my head, as I'm a simple fellow.

Last edited by Baltimore Sailor; 08-28-2008 at 10:31 AM.
Reply With Quote
  #23   IP: 206.181.246.34
Old 08-28-2008, 11:07 AM
SEMIJim SEMIJim is offline
Senior Member
 
Join Date: Oct 2007
Posts: 129
Thanks: 0
Thanked 1 Time in 1 Post
Quote:
Originally Posted by Baltimore Sailor View Post
It seems to me that so far we've established that if one has no mixed-voltage equipment, e.g. inverters, on board, using the shore ground for the AC system is OK. However, if you do have an inverter on board the AC must be grounded internally.
You're welcome to wire your boat however you like, but in my opinion, failing to connect the shore power safety ground to your boats "ground" creates a potentially lethal safety hazard. I, for one, would not care to be on a boat connected to shore power in such a way, nor be in a marina with any boat wired that way. Don Casey agrees with me.

Imagine hot somehow getting connected to your boats "ground," someone grabbing, say, a pushpit rail, leaning over and putting their hand in the water or grabbing an on-shore cleat bolted to something metal that's in the water or ground... or, it turns out, somebody swimming in the water nearby. Found this: This article appeared in our ABYC News in the Summer 2005 edition (Note: That's a PDF.) It would appear bonding AC safety ground to a boats DC ground is an ABYC standard.

Jim
Reply With Quote
  #24   IP: 76.7.126.120
Old 08-28-2008, 11:37 AM
Marian Claire's Avatar
Marian Claire Marian Claire is offline
Afourian MVP
 
Join Date: Aug 2007
Posts: 1,768
Thanks: 32
Thanked 129 Times in 94 Posts
Once again a thread on this forum has caused me to dig into and learn more about my boat. And for that I say Thanks. Dan
Reply With Quote
  #25   IP: 63.239.69.1
Old 08-28-2008, 12:55 PM
Baltimore Sailor's Avatar
Baltimore Sailor Baltimore Sailor is offline
Afourian MVP
 
Join Date: May 2007
Location: Monrovia, MD
Posts: 640
Thanks: 0
Thanked 6 Times in 6 Posts
My brain is reeling; I need a simple declarative statement. Should I have a ground lead connected to the engine block with the 12v grounds, and have that lead go from there to the ground of each and every outlet in the boat (only 1 so far), and thence to the ground connection on my boat's shore power inlet connector?

That sounds like what's being talked about, but I'm not sure. And I want to be as safe as possible.

To reiterate: engine block connection -> ground connection on AC outlet in boat -> ground connection on shore power inlet.

Yes?
Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump

Similar Threads
Thread Thread Starter Forum Replies Last Post
Thoughts on exciter line diodes (for engine runon when ignition switch is off) hcpookie Electrical 2 11-08-2009 10:32 AM
No power forward/Power in reverse forcenine Drive Train / Propellers 30 07-28-2008 12:47 PM
No power in gear Baltimore Sailor Troubleshooting 10 09-16-2007 09:27 PM
Power Loss in Forward ishmael Drive Train / Propellers 1 07-31-2007 10:14 PM
Loss of Power hobbit91 Troubleshooting 2 05-31-2007 06:59 AM


All times are GMT -4. The time now is 12:18 PM.


Powered by vBulletin® Version 3.8.9
Copyright ©2000 - 2024, vBulletin Solutions, Inc.


Universal® is a registered trademark of Westerbeke Corporation

Copyright © 2004-2024 Moyer Marine Inc.

All Rights Reserved