Question Bilge Safety

Adninistrator, I have reviewed many posts over the years and one thing keeps coming up that concerns me as far as safety is concerned. I have witnessed two gas related explosions on boats however both were on a power boat. In both instances neither was using the "Blower" to keep the engine-box/bilge vented. I have seen many posts regarding Co and smoke detectors in which they stated that they turned the Blower back on because of fumes. This scares the krap out of me.

My personal starting drill is to remove the key from the raw water valve while opening it which gives me a good opportunity to sniff the air. Then I start the blower prime the carb, close the choke and then stick my nose in the blower exhaust vent on the transom. If I smell no fuel I start the engine.

Whenever my engine is running SO IS THE BLOWER for safety and keeping a better flow of cool fresh air around the engine.

I would like to see a pole on how many actually cruise with the BLOWER off or on. I am also interested in seeing the comments that will follow.

Thanx, Dave Neptune
Reply With Quote
The Following User Says Thank You to Dave Neptune For This Useful Post:
TimBSmith (09-14-2020)
  #2   IP: 207.34.223.165
Old 09-09-2009, 04:23 PM
Bob.Griffin Bob.Griffin is offline
Senior Member
 
Join Date: Jun 2007
Posts: 47
Thanks: 0
Thanked 4 Times in 4 Posts
I share your concerns, one cannot be too careful with a gas engine on board. I have a gas fume detector located about 9 inches from the carb, fuel pump and Racor filter, and I actually test it periodically with a gas-soaked kleenex. I also leave the engine compartment door open (it slides) providing about a 6 inch by 12 inch gap, if I smell gas in the cabin I then check the engine compartment. While the engine is running I figure I have a good flow of air through the engine compartment door and out through 2 dorades on the stern. However, I am very close to wiring the bilge blower fan directly to the ignition so that it runs at all times when the engine is running, the only problem being that I need a parallel switched line to the blower so I can turn on before switching the ignition on, in the event of needing to clear any fumes during servicing for example.

Bob, s/v Dovetale
Reply With Quote
The Following User Says Thank You to Bob.Griffin For This Useful Post:
TimBSmith (09-14-2020)
  #3   IP: 151.204.250.196
Old 09-09-2009, 05:29 PM
smosher smosher is offline
Afourian MVP
 
Join Date: Jun 2006
Posts: 489
Thanks: 0
Thanked 36 Times in 35 Posts
I sniff for gas when I turn on the gas and the water. Then I turn on the blower. I will usually run the blower for several minutes before and after I start the engine. I had a small gas leak in the cover to the fram gas filter and its very noticeable when I went to turn on the gas.

I also have on my P30 two dorades for fresh air into the engine compartment.

Steve
Reply With Quote
  #4   IP: 206.40.166.218
Old 09-09-2009, 05:49 PM
Mark S's Avatar
Mark S Mark S is offline
Senior Member
 
Join Date: Sep 2008
Location: Marblehead MA
Posts: 421
Thanks: 0
Thanked 2 Times in 2 Posts
Quote:
Originally Posted by Dave Neptune View Post
Whenever my engine is running SO IS THE BLOWER for safety and keeping a better flow of cool fresh air around the engine.
Probably a good idea. Trouble is, most blowers were not designed to run for long and continuous periods of time. I have vents that bring in and take out air; I have the companionway hatch open; and I have the engine compartment doors open. This gives ample fresh air to the engine compartment. I run the blower before starting every time and I don't start without the "sniff test", but I do not run the blower all the time the engine is on. I should probably revisit this issue in my procedures and look for a blower that is capable of indefinite running.

Mark
Reply With Quote
  #5   IP: 75.197.31.175
Old 09-09-2009, 05:56 PM
Administrator's Avatar
Administrator Administrator is offline
MMI Webmaster
 
Join Date: Oct 2004
Location: Chestertown, MD (Langford Creek)
Posts: 2,166
Thanks: 1,335
Thanked 365 Times in 182 Posts
Quote:
actually cruise with the BLOWER off or on
Dave:

Do you mean while the engine is running, when it's not, or both?

Bill
Reply With Quote
  #6   IP: 71.118.13.238
Old 09-09-2009, 06:17 PM
Dave Neptune Dave Neptune is online now
Afourian MVP, Professor Emeritus
 
Join Date: Jan 2007
Location: Grove, Oklahoma
Posts: 5,038
Thanks: 713
Thanked 1,298 Times in 844 Posts
Thumbs up Blower

Bill, I actually mean on whenever the engine is running regardless of the dorade vents hatches etc. I have many friends whose boats I am leary of sailing with diesels as they just hit the starter and go. When I ask about the blower that they are equiped with they say it's a diesel and doesn't need to be vented~~~~BS.
I use a continuous duty type and it has been in service for at least 10~12 years now. I even let it run for a few minutes when I shut the motor down.

Thanx David
Reply With Quote
  #7   IP: 66.126.90.242
Old 09-09-2009, 07:14 PM
Kurt Kurt is offline
Senior Member
 
Join Date: Jun 2007
Posts: 290
Thanks: 0
Thanked 2 Times in 2 Posts
I have to climb into my lazarette, which is part of the engine compartment, to turn on the water and gas so I take this opportunity to take a sniff. I have had a gas leak from the carb before and the smell is undeniably obvious. I then turn on the blower for a couple of minutes and run it the entire time the engine is running. My last blower only lasted for 2 years, but hey - they are cheap!
Reply With Quote
  #8   IP: 142.68.254.34
Old 09-09-2009, 07:50 PM
rigspelt's Avatar
rigspelt rigspelt is offline
Afourian MVP
 
Join Date: May 2008
Posts: 1,186
Thanks: 0
Thanked 19 Times in 17 Posts
Our blower is very loud, obnoxious and an amperage hog. May need to rethink procedures.
__________________
1974 C&C 27
Reply With Quote
  #9   IP: 24.152.140.113
Old 09-09-2009, 08:01 PM
ndutton's Avatar
ndutton ndutton is offline
Afourian MVP
 
Join Date: May 2009
Location: Torrance, CA
Posts: 9,601
Thanks: 197
Thanked 2,206 Times in 1,423 Posts
My practice is to run the blower about five minutes prior to starting and continuously while the engine is running. In addition, I have the Xintex MB-1 Gas Fume Detector that emits a shrill alarm and automatically turns on the blower if combustible fumes are detected. The system shuts down the blower when the fumes are evacuated. I keep this system on at all times even when I'm not at the boat. It keeps an eye (nose??) on things when I can't. It's available at West and I recommend it highly.

Neil
77 Catalina 30
Reply With Quote
  #10   IP: 173.73.53.19
Old 09-09-2009, 08:20 PM
keelcooler keelcooler is offline
Senior Member
 
Join Date: Oct 2008
Location: McLean Va
Posts: 282
Thanks: 0
Thanked 4 Times in 4 Posts
As Dave said,incorporate sticking your face in the engine bay as part of your start up procedure (opening raw water cock). Any explosive fumes and you will know.
I shut the blower off when the engine starts. Run your blower for an extended time and fell how hot that sucker gets.
Mark is right, our under $100. blowers are not designed to run continuous.Our econo blowers are for intermittent cycles only.
Just like all electrical stuff in the motor bay the motors per Coast Guard must be shielded to prevent a spark source.
Overheat the blower motor and you may degrade the shielding. How many blowers have you herd squealing? They are worn out but still running. Our econo blower manufactures recommend replacement after eight or nine hundred hours.
When running you should have a natural venting duct,cowl and feel air flow at the motor duct end.
Most gas fume explosions occur right after refueling. This is the time to open the fuel tank hatch and religiously check fill,vent and tank surfaces for a wet spot or fumes.
We must not overlook electrical and raw fuel fires in are motor box.This risk is by far the most common.
All engine fires I have been involved in could not be extinguished by owner or crew.
All engine fires I have been involved in with an automatic haylon type extinguisher were put out before the operator even knew of a problem.
They work and that's why your insurer will offer a discount upon install.
Reply With Quote
  #11   IP: 71.243.21.66
Old 09-09-2009, 10:28 PM
Mark S's Avatar
Mark S Mark S is offline
Senior Member
 
Join Date: Sep 2008
Location: Marblehead MA
Posts: 421
Thanks: 0
Thanked 2 Times in 2 Posts
Quote:
Originally Posted by Dave Neptune View Post
I use a continuous duty type and it has been in service for at least 10~12 years now.
Dave, what do you have for a blower? I want one.

Mark
Reply With Quote
  #12   IP: 24.152.140.113
Old 09-09-2009, 11:35 PM
ndutton's Avatar
ndutton ndutton is offline
Afourian MVP
 
Join Date: May 2009
Location: Torrance, CA
Posts: 9,601
Thanks: 197
Thanked 2,206 Times in 1,423 Posts
All good points and I want a continuous duty blower too.

It seems to me that with the engine running, fuel pump pumping and fuel flowing, the possibility of a fuel leak is enhanced and at a time when I’m on deck rather than in a position to sniff the bilge. I’m still more comfortable with powered over natural ventilation and if my blower starts complaining I’ll replace it like any other worn out component.

It also seems to me that the blower and Halon extinguishing system serve different purposes. The blower is intended to remove dangerous fumes before something catastrophic happens while the Halon system minimizes the damage after the catastrophe. One system isn’t preferable to the other, they both perform essential functions.

Neil
77 Catalina 30
Reply With Quote
Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump

Similar Threads
Thread Thread Starter Forum Replies Last Post
Bilge Blower Placement swokrams General Interest 13 06-17-2008 11:27 AM
Bilge Blower COB General Interest 1 07-26-2007 05:32 PM
Redundant oil pressure safety switches? skhorleb Fuel System 1 05-19-2007 07:53 AM
Bilge water 78ranger Ranger 2 05-08-2007 09:16 PM
Emergency Bilge Pump (T in water intake) sailorken General Interest 0 11-05-2005 08:40 AM


All times are GMT -4. The time now is 02:26 AM.


Powered by vBulletin® Version 3.8.9
Copyright ©2000 - 2024, vBulletin Solutions, Inc.


Universal® is a registered trademark of Westerbeke Corporation

Copyright © 2004-2024 Moyer Marine Inc.

All Rights Reserved