Engine fire extinquisher system and fuses

I was wondering if any of you guys have experience with selecting and
installing a automatic fire extinquisher system for the engine compartment.
In the case of my Tartan 34c, the engine, batteries, regulators,battery
fuse and fuel tank are located in near proximity.

What type of automatic safety equipment is available?

Also with regard to Main battery fuse, are there intrinsically safe breakers
available?

Best Regards

Art
Reply With Quote
  #2   IP: 24.224.206.117
Old 12-19-2011, 01:00 PM
Mo's Avatar
Mo Mo is offline
Afourian MVP
 
Join Date: Jun 2007
Location: Halifax NS,
Posts: 4,468
Thanks: 292
Thanked 407 Times in 270 Posts
Smile 10 lb extinguishers ...

Art,
If everything is in a confined space it's relatively easy. For example, a 10lb dry chemical could be mounted in a lazarette and its nozzel through a bulkhead and into the engine compartment. Pull the pin and it would knock down any fire in that space.

The problem occurs when the space is large or there are no bulkheads actually enclosing the space. The dry chemical then may be dispersed too much to be effective. This is the situation on my boat. I have a 10 lb'er on one side of the lazarette and the nozzel pointed toward the engine...pull pin and squeeze. The whole area is not sealed off so it may or may not put a fire down first shot.

Proper safety regarding fuel issues should prevent "explosive" incidents. In the case of explosion these are, violent and immediate. You could not activate the device. The best you can do is PREVENT or put out a fire after... if you are able.

Most fires on boats are not explosive. However, they must be extinguished. The main problem is not having enough "umph" in the fire extinguisher. I'll phrase it like this...it's like going up against a machine gun with a .38 revolver. If the extinguisher is too small the chances of it working out for you are limited from the start.

Odyssey's fire extinguishers....(4) 10lb dry chemical and (2) 5 lbs dry chemical..the only reason there are 5 lb extinguishers on the boat is because she came with them. One 10 lb'er can knock down a decent fire....the other are just in case.
Attached Images
 
__________________
Mo

"Odyssey"
1976 C&C 30 MKI

The pessimist complains about the wind.
The optimist expects it to change.
The realist adjusts the sails.
...Sir William Arthur Ward.
Reply With Quote
  #3   IP: 72.71.243.66
Old 12-19-2011, 01:19 PM
ArtJ ArtJ is offline
 
Join Date: Sep 2009
Posts: 2,175
Thanks: 218
Thanked 65 Times in 50 Posts
Thanks for the input Maurice

You are right, fuel related explosions are immediate and probably a
automatic fire extinqusher system would not be fast enough to prevent
a fire or explosion. Besides that, they are subject to possible accidental
activation and could create havoc with components.
I was hoping that some sort of foam bath for the engine could prevent
this issue. Maybe it could prevent a explosion when a fire occurred prior
to the explosion.
I have previously installed a fume detector alarm, possibly
that combined with a installed extinquisher as you suggestwould give time to
spray the compartment and prevent explosion.

The other method, as you mention, is to carefully monitor wiring,
fuses.

A few years back, I installed a 100A? fuse in the primary ckt of the
battery. The fear I have is that this fuse could catch fire and
not blow clean. There must be breakers or fuses that could
prevent this.

Regards

Arr
Reply With Quote
  #4   IP: 96.244.238.12
Old 12-19-2011, 09:58 PM
msauntry's Avatar
msauntry msauntry is offline
 
Join Date: May 2008
Location: Annapolis, MD
Posts: 506
Thanks: 0
Thanked 4 Times in 4 Posts
An excellent thread to open up! My thoughts turn to the Fireboy automatic units. I was looking them up and they have models to cover various cubic footage. They have diesel and gasoline specific models and the agent is not supposed to harm or contaminate the boat after discharge. I know the dry chemical ones can damage and corrode any electronics. They trigger at a certain temperature and/or manually.

I do not know of any systems that will prevent a fire, only react to one already in progress. This is where the fume sniffers would come in handy. Anybody got specs on a fume sniffer that is comercially available? I know some of you have Pearsons that came with them installed but that part manufacturer is no longer running.
Reply With Quote
  #5   IP: 50.101.48.152
Old 12-19-2011, 10:08 PM
67c&ccorv's Avatar
67c&ccorv 67c&ccorv is offline
Afourian MVP
 
Join Date: Dec 2008
Location: London, ON
Posts: 1,559
Thanks: 4
Thanked 9 Times in 9 Posts
My 67 C&C Corvette had an automatic Halon fire extinguisher system mounted in the engine compartment but I removed it as it had long ago passed it's final inspection date.

Reply With Quote
  #6   IP: 151.200.26.29
Old 12-19-2011, 10:59 PM
sastanley's Avatar
sastanley sastanley is offline
Afourian MVP
 
Join Date: Sep 2008
Location: Solomons, MD
Posts: 6,986
Thanks: 1,133
Thanked 603 Times in 443 Posts
Micah, I think Neil has a sniffer in his boat. That might be for the CNG/propane system though..I cannot recall at this time.
__________________
-Shawn
"Holiday" - '89 Alura 35 #109
"Twice Around" - '77 C-30, #511 with original A-4 & MMI manifold - SOLD! (no longer a two boat owner!!)
http://www.moyermarine.com/forums/signaturepics/sigpic3231_6.gif
Reply With Quote
  #7   IP: 72.83.115.32
Old 12-20-2011, 12:09 AM
edwardc's Avatar
edwardc edwardc is offline
Afourian MVP
 
Join Date: Aug 2009
Location: Laurel, MD
Posts: 2,491
Thanks: 154
Thanked 593 Times in 387 Posts
Quote:
Originally Posted by ArtJ View Post

A few years back, I installed a 100A? fuse in the primary ckt of the
battery. The fear I have is that this fuse could catch fire and
not blow clean. There must be breakers or fuses that could
prevent this.

Regards

Arr
The ANL fuses, sold by Defender and others, are ignition protected and rated for gasoline boats:

http://www.defender.com/product.jsp?...931&id=1334628
__________________
@(^.^)@ Ed
1977 Pearson P-323 "Dolce Vita"
with rebuilt Atomic-4

Reply With Quote
  #8   IP: 72.71.243.66
Old 12-20-2011, 12:10 PM
ArtJ ArtJ is offline
 
Join Date: Sep 2009
Posts: 2,175
Thanks: 218
Thanked 65 Times in 50 Posts
Quote:
Originally Posted by edwardc View Post
The ANL fuses, sold by Defender and others, are ignition protected and rated for gasoline boats:

http://www.defender.com/product.jsp?...931&id=1334628
I (mistakenly?) in the past took ignition protected to mean it somehow
protected engine ignition electrical parts, should I have read this
as FUSE IS FLAME IGNiTION PROOF as in flamming of the fuse and surrounding fumes?

Regards

Art
Reply With Quote
  #9   IP: 205.188.117.74
Old 12-21-2011, 02:11 AM
Dockside Charlie Dockside Charlie is offline
Senior Member
 
Join Date: Nov 2011
Posts: 11
Thanks: 0
Thanked 0 Times in 0 Posts
Ignition protected is intended to mean the electrical componant,bat-chgr,pump,alt,dist,str,blwr,fuse,etc.in it's normal function,could possibly create a fuel source to ignite/combust(hydrg-gas from batteries,gasoline fumes,diesel or lube oil leaks on heated surfaces creating flammable vapors,propane)less likely but not garrenteed to ignite unintentionaly or expectedly.These units are resistant to,not infallible and do not relate to points and plugs firing the engines running.Safety is the focus.
Reply With Quote
  #10   IP: 128.183.140.38
Old 12-22-2011, 09:55 AM
edwardc's Avatar
edwardc edwardc is offline
Afourian MVP
 
Join Date: Aug 2009
Location: Laurel, MD
Posts: 2,491
Thanks: 154
Thanked 593 Times in 387 Posts
Quote:
Originally Posted by ArtJ View Post
I (mistakenly?) in the past took ignition protected to mean it somehow
protected engine ignition electrical parts, should I have read this
as FUSE IS FLAME IGNiTION PROOF as in flamming of the fuse and surrounding fumes?

Regards

Art
Ignition protected means it will not ignite a flamable vapor mixture.


Funny story: Years ago, when I worked for the Navy dept, we had these big, heavy black plastic flashlights that were ignition protected, but back then, they were labled as "Explosion Proof". One of my co-workers noticed that for the first time and said "Really? That's cool!", and proceeded to test it by smashing the flashlight on the edge of the workbench!

The look on his face was priceless when the flashlight head shattered into a dozen pieces!
__________________
@(^.^)@ Ed
1977 Pearson P-323 "Dolce Vita"
with rebuilt Atomic-4

Reply With Quote
  #11   IP: 71.168.64.84
Old 05-23-2012, 12:14 PM
ArtJ ArtJ is offline
 
Join Date: Sep 2009
Posts: 2,175
Thanks: 218
Thanked 65 Times in 50 Posts
Attention Neil and All

HI guys

Would really appreciate input on the Fireboy extinquisher so I can
decide whether or not it can be safely installed.

Thanks very very much

Art
Reply With Quote
  #12   IP: 24.152.131.155
Old 05-23-2012, 09:17 PM
ndutton's Avatar
ndutton ndutton is offline
Afourian MVP
 
Join Date: May 2009
Location: Torrance, CA
Posts: 9,601
Thanks: 197
Thanked 2,206 Times in 1,423 Posts
My $0.02

I searched online and found the installation instructions. Essentially this is the same as the old Halon systems with a different smothering gas and as I understand it, there are four things to consider:
  1. As you said, you have to find a place to mount it. I believe it should sense and smother the compartment where a fire is most likely to start, not where it may migrate to. To me this means high in the engine compartment. That is where the fuel is launched out of a closed system (carb) and where the likely ignition source exists. I'm not saying there aren't other places where fumes could collect and ignite but you have to go with the law of averages. You can't count on the system to extinguish a fire in an adjoining compartment. Some smothering agent may find its way there but probably not enough to be effective.
  2. The reason they advise against athwartships horizontal mounting is on one tack the dispersing head will be below the tank and they caution strongly to mount it with the head higher than the tank. I expect the smothering agent is a liquid inside the tank that vaporizes on pressure drop (activation) and they want to be sure you're dispensing vapor rather than liquid in the compartment. Since you say there is no space inside the engine compartment, could it be mounted outside the compartment with only the sensor and dispersing head inside? Maybe camouflage it with a cover of some sort?
  3. For a proper system you must wire the blower through the pressure switch on the unit. They use the switch for the indicator light but have instructions on how to wire the blower through it. Once the agent is dispensed you don't want the blower removing it and ventilating the space with fresh oxygen carrying air.
  4. You might want to take some compartment temperature measurements underway to see what the ambient temperature actually is. The gauge and compartment temps should be very different. Of course, avoid mounting the unit in the vicinity of or above the exhaust hot section. Heat rises.
__________________
Neil
1977 Catalina 30
San Pedro, California
prior boats 1987 Westsail 32, 1970 Catalina 22
Had my hands in a few others
Reply With Quote
  #13   IP: 71.168.64.84
Old 05-24-2012, 06:58 AM
ArtJ ArtJ is offline
 
Join Date: Sep 2009
Posts: 2,175
Thanks: 218
Thanked 65 Times in 50 Posts
Quote:
Originally Posted by ndutton View Post
I searched online and found the installation instructions. Essentially this is the same as the old Halon systems with a different smothering gas and as I understand it, there are four things to consider:
  1. As you said, you have to find a place to mount it. I believe it should sense and smother the compartment where a fire is most likely to start, not where it may migrate to. To me this means high in the engine compartment. That is where the fuel is launched out of a closed system (carb) and where the likely ignition source exists. I'm not saying there aren't other places where fumes could collect and ignite but you have to go with the law of averages. You can't count on the system to extinguish a fire in an adjoining compartment. Some smothering agent may find its way there but probably not enough to be effective.
  2. The reason they advise against athwartships horizontal mounting is on one tack the dispersing head will be below the tank and they caution strongly to mount it with the head higher than the tank. I expect the smothering agent is a liquid inside the tank that vaporizes on pressure drop (activation) and they want to be sure you're dispensing vapor rather than liquid in the compartment. Since you say there is no space inside the engine compartment, could it be mounted outside the compartment with only the sensor and dispersing head inside? Maybe camouflage it with a cover of some sort?
  3. For a proper system you must wire the blower through the pressure switch on the unit. They use the switch for the indicator light but have instructions on how to wire the blower through it. Once the agent is dispensed you don't want the blower removing it and ventilating the space with fresh oxygen carrying air.
  4. You might want to take some compartment temperature measurements underway to see what the ambient temperature actually is. The gauge and compartment temps should be very different. Of course, avoid mounting the unit in the vicinity of or above the exhaust hot section. Heat rises.
Thank you for the information Neil
Unfortunately, I do not have room in the tiny Tartan34C engine box
for the extinquisher. Additionally, I am concerned about the ambient
temperature inside this tiny box reaching over 175 degrees easily in
normal operation. Bottom line: It's a nice unit if you can safely install
it which I cannot. The hazard outweighs it's value, so I am going to
return it.

Thanks again and best Regards

Art
Reply With Quote
  #14   IP: 206.125.176.5
Old 05-24-2012, 09:09 AM
sastanley's Avatar
sastanley sastanley is offline
Afourian MVP
 
Join Date: Sep 2008
Location: Solomons, MD
Posts: 6,986
Thanks: 1,133
Thanked 603 Times in 443 Posts
Art, My buddy's fancy Beneslow 343 has a simple plastic one-way hole cut into the stairs for jamming an extinguisher into the engine box. Anyway to remotely mount the system and plumb it into the engine box that way?

Art, on second thought, I googled "fire extinguisher port", and found this good Boat US article which says blindly spraying into an engine box is useless, unless it is a gaseous type that removes the oxygen.

http://www.boatus.com/seaworthy/swybf.asp
__________________
-Shawn
"Holiday" - '89 Alura 35 #109
"Twice Around" - '77 C-30, #511 with original A-4 & MMI manifold - SOLD! (no longer a two boat owner!!)
http://www.moyermarine.com/forums/signaturepics/sigpic3231_6.gif

Last edited by sastanley; 05-24-2012 at 09:19 AM. Reason: add link
Reply With Quote
  #15   IP: 71.168.64.84
Old 05-24-2012, 03:34 PM
ArtJ ArtJ is offline
 
Join Date: Sep 2009
Posts: 2,175
Thanks: 218
Thanked 65 Times in 50 Posts
Quote:
Originally Posted by sastanley View Post
Art, My buddy's fancy Beneslow 343 has a simple plastic one-way hole cut into the stairs for jamming an extinguisher into the engine box. Anyway to remotely mount the system and plumb it into the engine box that way?

Art, on second thought, I googled "fire extinguisher port", and found this good Boat US article which says blindly spraying into an engine box is useless, unless it is a gaseous type that removes the oxygen.

http://www.boatus.com/seaworthy/swybf.asp
Thanks for the reply and suggestion Shawn. The Tartan 34 C
has the engine sitting in the middle of the main salon under a small
settee and half buried in the bilge. There is no adjacent bulkhead other
than the battery box which is jammed full. I have returned the
Extinquisher to Hamilton Marine for credit.

Best Regards and Thanks

Art
Reply With Quote
Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump

Similar Threads
Thread Thread Starter Forum Replies Last Post
Seized engine turns over!...but.... mbettman Troubleshooting 10 10-28-2010 05:11 AM


All times are GMT -4. The time now is 06:44 AM.


Powered by vBulletin® Version 3.8.9
Copyright ©2000 - 2024, vBulletin Solutions, Inc.


Universal® is a registered trademark of Westerbeke Corporation

Copyright © 2004-2024 Moyer Marine Inc.

All Rights Reserved